I thought I remembered something in the OSHA requirements about the amount of stuff stored. Here is a copy of a section of OSHA rules relating to flammable storage. - Hope it helps. This goes to show that my memory has slipped. The cabinet mentioned in my earlier post was not Sheetrock, but two layers of plywood. I think my guys put Sheetrock on the outside of the plywood. I now remember the rabbeted joints. [see paragraph (b)(2)(I) below]
1926.152 - Flammable and combustible liquids.
(a) General requirements.
(a)(1) Only approved containers and portable tanks shall be used for storage and handling of flammable and combustible liquids. Approved metal safety cans shall be used for the handling and use of flammable liquids in quantities greater than one gallon, except that this shall not apply to those flammable liquid materials which are highly viscid (extremely hard to pour), which may be used and handled in original shipping containers. For quantities of one gallon or less, only the original container or approved metal safety cans shall be used for storage, use, and handling of flammable liquids.
(a)(2) Flammable or combustible liquids shall not be stored in areas used for exits, stairways, or normally used for the safe passage of people.
(b) Indoor storage of flammable and combustible liquids.
(b)(1) No more than 25 gallons of flammable or combustible liquids shall be stored in a room outside of an approved storage cabinet. For storage of liquefied petroleum gas, see 1926.153.
(b)(2) Quantities of flammable and combustible liquid in excess of 25 gallons shall be stored in an acceptable or approved cabinet meeting the following requirements:
(b)(2)(i) Acceptable wooden storage cabinets shall be constructed in the following manner, or equivalent: The bottom, sides, and top shall be constructed of an exterior grade of plywood at least 1 inch in thickness, which shall not break down or delaminate under standard fire test conditions. All joints shall be rabbeted and shall be fastened in two directions with flathead wood screws. When more than one door is used, there shall be a rabbeted overlap of not less than 1 inch. Steel hinges shall be mounted in such a manner as to not lose their holding capacity due to loosening or burning out of the screws when subjected to fire. Such cabinets shall be painted inside and out with fire retardant paint.
(b)(2)(ii) Approved metal storage cabinets will be acceptable.
(b)(2)(iii) Cabinets shall be labeled in conspicuous lettering, "Flammable-Keep Fire Away."
(b)(3) Not more than 60 gallons of flammable or 120 gallons of combustible liquids shall be stored in any one storage cabinet. Not more than three such cabinets may be located in a single storage area. Quantities in excess of this shall be stored in an inside storage room.
(f) Handling liquids at point of final use.
(f)(1) Flammable liquids shall be kept in closed containers when not actually in use.
(f)(2) Leakage or spillage of flammable or combustible liquids shall be disposed of promptly and safely.
(f)(3) Flammable liquids may be used only where there are no open flames or other sources of ignition within 50 feet of the operation, unless conditions warrant greater clearance.
Here is a link to the OSHA pages - http://www.ehso.com/oshaConstruction_F.htm
1926.152 - Flammable and combustible liquids.
(a) General requirements.
(a)(1) Only approved containers and portable tanks shall be used for storage and handling of flammable and combustible liquids. Approved metal safety cans shall be used for the handling and use of flammable liquids in quantities greater than one gallon, except that this shall not apply to those flammable liquid materials which are highly viscid (extremely hard to pour), which may be used and handled in original shipping containers. For quantities of one gallon or less, only the original container or approved metal safety cans shall be used for storage, use, and handling of flammable liquids.
(a)(2) Flammable or combustible liquids shall not be stored in areas used for exits, stairways, or normally used for the safe passage of people.
(b) Indoor storage of flammable and combustible liquids.
(b)(1) No more than 25 gallons of flammable or combustible liquids shall be stored in a room outside of an approved storage cabinet. For storage of liquefied petroleum gas, see 1926.153.
(b)(2) Quantities of flammable and combustible liquid in excess of 25 gallons shall be stored in an acceptable or approved cabinet meeting the following requirements:
(b)(2)(i) Acceptable wooden storage cabinets shall be constructed in the following manner, or equivalent: The bottom, sides, and top shall be constructed of an exterior grade of plywood at least 1 inch in thickness, which shall not break down or delaminate under standard fire test conditions. All joints shall be rabbeted and shall be fastened in two directions with flathead wood screws. When more than one door is used, there shall be a rabbeted overlap of not less than 1 inch. Steel hinges shall be mounted in such a manner as to not lose their holding capacity due to loosening or burning out of the screws when subjected to fire. Such cabinets shall be painted inside and out with fire retardant paint.
(b)(2)(ii) Approved metal storage cabinets will be acceptable.
(b)(2)(iii) Cabinets shall be labeled in conspicuous lettering, "Flammable-Keep Fire Away."
(b)(3) Not more than 60 gallons of flammable or 120 gallons of combustible liquids shall be stored in any one storage cabinet. Not more than three such cabinets may be located in a single storage area. Quantities in excess of this shall be stored in an inside storage room.
(f) Handling liquids at point of final use.
(f)(1) Flammable liquids shall be kept in closed containers when not actually in use.
(f)(2) Leakage or spillage of flammable or combustible liquids shall be disposed of promptly and safely.
(f)(3) Flammable liquids may be used only where there are no open flames or other sources of ignition within 50 feet of the operation, unless conditions warrant greater clearance.
Here is a link to the OSHA pages - http://www.ehso.com/oshaConstruction_F.htm