power pro ground fault

Posted: Sat Feb 09, 2019 4:54 pm
by woodennickel
Are ground fault breaker more sensitive than a ground fault outlet? I installed a dedicated circuit on a gfi. This one trips immediately on power up. You can plug in to a ground fault outlet and everything seems fine.

Re: power pro ground fault

Posted: Sat Feb 09, 2019 6:13 pm
by wa2crk
It should not make a difference. Get a gfi from an electrical supply house that deals with the trade. Get one that is certified hospital grade. They are more tolerant of strong rd fields.
Bill V

Re: power pro ground fault

Posted: Sat Feb 09, 2019 6:58 pm
by sehast
I have had both and the GFI circuit breaker does seem to be more sensitive. But I don't use either on the PowerPro. It seemed to trip both the wall plug as well as the circuit breaker. I finally just used a 220V service line.

Re: power pro ground fault

Posted: Sat Feb 09, 2019 7:14 pm
by reible
The powerpro manual has some information on using it with GFI. I don't recall what it says but if you can't find it let me know and I will dig out my manual and provide you with it.

Ed

Re: power pro ground fault

Posted: Sat Feb 09, 2019 9:18 pm
by woodennickel
I got to digging around in the panel and found we had wired the neutral to the neutral bar instead of the load side of the breaker. I appreciate all those who tried to help. Thanks a bunch.

Re: power pro ground fault

Posted: Sun Feb 10, 2019 12:31 pm
by JPG
woodennickel wrote:I got to digging around in the panel and found we had wired the neutral to the neutral bar instead of the load side of the breaker. I appreciate all those who tried to help. Thanks a bunch.
I surmise that ANYTHING turned on while plugged into that circuit tripped the breaker.