I am going to add some electric baseboard heat to my soon to be insulated and “sound proofed” basement shop. Thirty solar panels just went up on my roof! My question is, at 240 volts, what is the maximum wattage that 12 gauge can safely handle?
As always, thanks in advance.
Chris
Chris Neilan

Shopsmith Mark 7, Shopsmith Mark V 1982, shortened, Shopsmith 10 ER; Craftsman table saw (1964); Powermatic 3520B lathe
User avatar
ChrisNeilan
Platinum Member
Posts: 1461
Joined: Sun Oct 27, 2013 5:30 pm
Location: Waterford, Connecticut
Contact:

Re: Adding heat- wiring question

Post by ChrisNeilan »

Thanks Dusty. I plan on installing two 1500 watt heaters. I’ll run the wire prior to hitting the walls with spray foam insulation. Great vapor barrier .
Chris Neilan

Shopsmith Mark 7, Shopsmith Mark V 1982, shortened, Shopsmith 10 ER; Craftsman table saw (1964); Powermatic 3520B lathe
User avatar
JPG
Platinum Member
Posts: 34631
Joined: Wed Dec 10, 2008 7:42 pm
Location: Lexington, Ky (TAMECAT territory)

Re: Adding heat- wiring question

Post by JPG »

#12 awg is 'rated' for 20 A. The voltage is irrelevant, but typical romex etc. is 'rated' 600v.

Did Dusty say something??? :confused:
╔═══╗
╟JPG ╢
╚═══╝

Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10
E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
User avatar
dusty
Platinum Member
Posts: 21368
Joined: Wed Nov 22, 2006 6:52 am
Location: Tucson (Wildcat Country), Arizona

Re: Adding heat- wiring question

Post by dusty »

JPG wrote:#12 awg is 'rated' for 20 A. The voltage is irrelevant, but typical romex etc. is 'rated' 600v.

Did Dusty say something??? :confused:
Yes I did but I deleted it. After rereading my reference, I was uncertain about the number I stated.
"Making Sawdust Safely"
Dusty
Sent from my Dell XPS using Firefox.
User avatar
dusty
Platinum Member
Posts: 21368
Joined: Wed Nov 22, 2006 6:52 am
Location: Tucson (Wildcat Country), Arizona

Re: Adding heat- wiring question

Post by dusty »

JPG wrote:#12 awg is 'rated' for 20 A. The voltage is irrelevant, but typical romex etc. is 'rated' 600v.

Did Dusty say something??? :confused:
Yes I did but I deleted it. After rereading my reference, I was uncertain about the number I stated.

https://www.icmag.com/modules/Tutorials ... y/1655.htm

Local Code????
"Making Sawdust Safely"
Dusty
Sent from my Dell XPS using Firefox.
User avatar
JPG
Platinum Member
Posts: 34631
Joined: Wed Dec 10, 2008 7:42 pm
Location: Lexington, Ky (TAMECAT territory)

Re: Adding heat- wiring question

Post by JPG »

After reading what dusty referenced;

I would recommend staying below 16A for electric heating supply wiring since long term loading is likely. I would also recommend larger wire size if run is very long.

BTW at 240v @ 16A(resistive) = 3840 W.

2 x 1500W will be safely supplied with #12, but #10 is more gooder if run is very far. 10-2(with #10 ground) will suffice. 10-3(w/o ground) will also do if ground wire is painted/marked. Local codes need to be strictly adhered to fer sure with this project!!!!!!!!!
╔═══╗
╟JPG ╢
╚═══╝

Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10
E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
User avatar
JPG
Platinum Member
Posts: 34631
Joined: Wed Dec 10, 2008 7:42 pm
Location: Lexington, Ky (TAMECAT territory)

Re: Adding heat- wiring question

Post by JPG »

P.S. I would use #10-2 BX for supply wiring, NOT romex. I assume it still exists.
╔═══╗
╟JPG ╢
╚═══╝

Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10
E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
SpencerWhite
Silver Member
Posts: 8
Joined: Wed Apr 20, 2022 3:10 pm

Re: Adding heat- wiring question

Post by SpencerWhite »

After you’ve figured out the usage, you need to select the technology.
Last edited by SpencerWhite on Sat Jul 23, 2022 4:04 am, edited 2 times in total.
User avatar
ChrisNeilan
Platinum Member
Posts: 1461
Joined: Sun Oct 27, 2013 5:30 pm
Location: Waterford, Connecticut
Contact:

Re: Adding heat- wiring question

Post by ChrisNeilan »

Well, time flies! I did run 10 gauge wire, but never installed any heat. With all the insulation I installed, and the fact that my furnace lives nearby, the temperature never got below 65 degrees! My sleeve unit AC has a heat function, but I only turned it on once over the winter just to see if it works!
Chris Neilan

Shopsmith Mark 7, Shopsmith Mark V 1982, shortened, Shopsmith 10 ER; Craftsman table saw (1964); Powermatic 3520B lathe
Hobbyman2
Platinum Member
Posts: 2660
Joined: Wed Feb 01, 2017 12:52 am
Location: Ohio

Re: Adding heat- wiring question

Post by Hobbyman2 »

Any pro's and or cons on the solar panel system so far ? we have been tossing around the idea , it just worries me during the winter when the panels would be covered or have less hrs to charge the batteries . one person mentioned converting to LED lighting to reduce the stress on the system .