DLB wrote
]Um, no. Sorry if that was misleading. My shop is in my garage. What I was trying to say is that most of our shops are either in a garage or basement or other facility that, as of the 2020 NEC revision, require GFCI. The wettest location I've ever used for my shop was a basement though, and it seemed strange to me that at the time GFCI was not required there but it was required in the garage. The GFCI requirements, as well as the AFCI requirements, seem to continuously expand. Perhaps there is a lobby involved.
At least some hard-wired equipment is now included. Specific examples are HVAC and pool pumps. Also a range if it is within 6' of a sink.
- David
David,
Thanks. I hadn't reviewed the NEC in awhile so your post prompted me to investigate further and I learned a few new things from this. The NEC is complex and ever changing/expanding, so what follows is only my understanding of it and not advice for anyone (full disclaimer). I don't have the 2020 NEC to read ($$$), but just going off of changes posted online this is what I see. There is a really good summary document of the 2020 specific changes linked below (file was too large to post on the forum). What I found interesting was page 5 that has a useful table for detailing the "basic" requirements for where a GFCI or AFCI are required in different parts of the house. It shows that every receptacle in bedrooms now need both a GFCI and AFCI. Of course this is the latest NEC and many cities are slow to adopt the latest NEC, so if you are remodeling you still have to find out if these new rules apply to you yet.
The pool pump one is interesting and in my case doesn't apply. Rule 680.21(C) has been changed from the 2017 version and now only outlets used to connect pool pumps of 150V or less require a GFCI. It does look like the NEC slightly relaxed the GFCI requirement on pool pump motors from 2017->2020. Here out west the vast majority of pool pumps are direct connect (not on an outlet) and run on 240V so no GFCI required on pool pump motors here. For HVAC, rule 210.63 requires GFCI for outlets near HVAC equipment so this really only applies to the 120V outlet (for service) next to your furnace/AC in the attic as an example, i.e. it doesn't apply to direct connect 240V equipment (such as furnace/AC/heat pump/air handler). Lastly, I checked the garage section and again it only applies to 120V or 240V outlets in garages and anything direct connected is exempted. I just wanted to point out that the NEC does differentiate between direct connect versus items plugged into outlets so I am 99% certain any tool that is direct wired in a shop doesn't require GFCI/AFCI. Of course if one has a particularly damp basement or garage it may be prudent to install a GFCI anyway. Remember the overarching theme of GFCI protection has to do with avoiding electrocution from things you are in close proximity to and really only things that you touch AND are near a sink/pool, etc. which is why the 6' from water source is often in the requirements. If you have a big enough dust collector that is 240V and likely direct connected do you ever really touch the equipment while it is in operation? Electrocution risk is pretty darn low on a properly wired dust collector, even in a damp basement/garage where your only real connection to it is a plastic hose connected to your equipment. On the other hand, a tablesaw in a damp environment may be more of a risk for you since you are near it and touching it fairly regularly. NEC is clear for it...requires a GFCI if powered from outlet, but direct connect is still exempt
based on my understanding of the NEC. However, most people will plug in a tablesaw so that it can be mobile so GFCI needed.
Another interesting addition was in 230.67 where new construction or replacement of a service panel on an existing house now requires a whole house surge protector to be installed at the service panel to protect electronics.
List of 2020 NEC Changes:
https://www.eaton.com/content/dam/eaton/products/residential/electrical-safety/electrical-safety-national-electrical-code-2020-br1610048en.pdf
2017 vs. 2020 NEC regarding pool pumps:
https://www.electricallicenserenewal.com/Electrical-Continuing-Education-Courses/NEC-Content.php?sectionID=958.0