robfish wrote:I watched Dusty's video and have a much more clear idea of what I'll be looking for when I do my testing.
If I understand correctly, if I feed my Shopsmith with a 15 amp breaker connected to 12 AWG wire, there's a chance I'll blow the breaker because the Shopsmith is trying to draw more amps than the breaker's rating, but I probably won't damage the Shopsmith.
On the other hand, if I were to feed my Shopsmith with a 20 amp breaker connected to a really long run of 14 AWG, I probably wouldn't blow the breaker, but I could damage the Shopsmith because the long run of thin wire wouldn't be able to transmit the amount of amps required to drive the Shopsmith.
I'm wonder what kind of damage would be caused in the second scenario, and why.
Thanks!
Rob
Oh... I am going to follow Dusty's suggestion on replacing the Shopsmith's power cord with a heftier SO cord and suspect I'll end up running a new 20 amp circuit with 12 AWG wire to a new electrical outlet on the side of the house closest to the garage, and then use a 20 amp 50' extension cord whenever I work with the Shopsmith. I believe the 20 amp extension cord is made with 10 gauge wire.
Unless you persist in trying to run under this condition, you most likely would do no damage to the Shopsmith. The extension cord, however, might be another story. It would get hot and your power meter will be spinning faster. The power company will be happier.
Again, watch the voltage and listen to the Shopsmith to see what it is doing. If the voltage stays up at or near to 115 vac, the Shopsmith will be content.