Are ground fault breaker more sensitive than a ground fault outlet? I installed a dedicated circuit on a gfi. This one trips immediately on power up. You can plug in to a ground fault outlet and everything seems fine.
User avatar
wa2crk
Platinum Member
Posts: 3080
Joined: Sat Jul 22, 2006 7:37 am
Location: Leesburg, Fl

Re: power pro ground fault

Post by wa2crk »

It should not make a difference. Get a gfi from an electrical supply house that deals with the trade. Get one that is certified hospital grade. They are more tolerant of strong rd fields.
Bill V
sehast
Gold Member
Posts: 497
Joined: Sun Apr 12, 2015 6:53 pm
Location: Milpitas, CA

Re: power pro ground fault

Post by sehast »

I have had both and the GFI circuit breaker does seem to be more sensitive. But I don't use either on the PowerPro. It seemed to trip both the wall plug as well as the circuit breaker. I finally just used a 220V service line.
User avatar
reible
Platinum Member
Posts: 11283
Joined: Thu Jul 20, 2006 12:08 pm
Location: Aurora, IL

Re: power pro ground fault

Post by reible »

The powerpro manual has some information on using it with GFI. I don't recall what it says but if you can't find it let me know and I will dig out my manual and provide you with it.

Ed
{Knight of the Shopsmith} [Hero's don't wear capes, they wear dog tags]
woodennickel
Silver Member
Posts: 13
Joined: Tue Jan 01, 2019 2:59 pm

Re: power pro ground fault

Post by woodennickel »

I got to digging around in the panel and found we had wired the neutral to the neutral bar instead of the load side of the breaker. I appreciate all those who tried to help. Thanks a bunch.
User avatar
JPG
Platinum Member
Posts: 35430
Joined: Wed Dec 10, 2008 7:42 pm
Location: Lexington, Ky (TAMECAT territory)

Re: power pro ground fault

Post by JPG »

woodennickel wrote:I got to digging around in the panel and found we had wired the neutral to the neutral bar instead of the load side of the breaker. I appreciate all those who tried to help. Thanks a bunch.
I surmise that ANYTHING turned on while plugged into that circuit tripped the breaker.
╔═══╗