I agree that 25 feet of 12 AWG cord should work fine. The resistance of 12AWG copper wire is 0.0017 Ohms/foot. The electricity will have to travel 50' round-trip in your 25' cord, so the total series resistance of the wire is 50 * .0017 = 0.085 Ohms. Assuming a 13.2 Amp continuous rated current for your Mark V motor, the voltage drop across the additional wire is 13.2 * 0.085 = 1.1V. Not a problem.GG0452 wrote: ↑Thu Mar 13, 2025 1:31 pm I feel that the 25 feet of 12 gauge extension is more than adequate for several reasons. 1. SS recommends 12 gauge wire for a 50 foot extension cord. 2. I ran my Mark v for 40 years using a 50 foot 14 gauge extension cord without any problems. 3. The cord is exposed, lies on the floor, and can be monitored for overheating. The only issue, as i see it, is start up time and that does not seem to be a problem. Heck, my house vacuum runs on 18 gauge wire and get hot every time the vacuum is used. BTW when is first got my Mark V i ran it on a 15 amp fused circuit. That was a pain and why i had a breaker box installed and the 30 amp 10 gauge wire circuit for the SS (and i think at the time local code was 20 amp circuit on 14 gauge wire and now it is 15 amps).
At the 54V startup surge current that I measured on my own Mark V, the voltage drop across the extension cord would still be only 54A * 0.085 Ohms = 4.6V. Even factoring in the 30 milliohm rated maximum contact resistance of Nema 5-15 plugs and receptacles, the worst-case voltage drop during the startup surge is 54 * (0.085 + 0.030) = 6.21V, or roughly 5% of the nominal line voltage. Again, not a problem -- that's well within specs for an induction motor.