Using two conductors in parallel to 'increase' the capacity of a branch circuit IS a bad idea!dusty wrote:Are we talking about serving two or more circuits with the same breaker OR
are we talking about using two wires for the same feed (like two #14 is better than one #12).
Both seem like a NO NO to me.
Having more than one path is not uncommon. A branch circuit may go direct from the breaker to a device or junction box and be spliced into two separate (sub) branches. The splicing may also be done within the breaker panel. Consider what is done on a lighting branch circuit: A feed(from the breaker or another device box) connects to the switch and the neutral is spliced to a pair of conductors going to the 'light'(the second conductor connects between the light and the switch). Both the hot and the neutral may also be spliced to another pair which feeds device box(es) downstream.
Keep in mind the breaker is sized to protect the conductors by limiting the maximum current. If a circuit is split, each separate path is more than adequately protected as long as the breaker IS properly sized for the conductors used(bigger wire is ok, smaller wire is NOT!).
Using parallel conductors is an acceptable method(IMHO) of decreasing the voltage drop on a LONG run as long as the breaker is the correct size for the wires used. Any run doing this should be side by side. It is probably cheaper to just use the larger size wire(and less prone to later mis-understanding).
I have rambled here at the possible expense of clarity. If confused tell me, I will try again by narrowing things down a bit.
Keep one hand in yer pocket when the other is IN the box!? Stand on dry floor(preferably insulated)!:eek: