From what I have been told, by my wife's brother, this 10ER was definitely powered by 220v. The motor plate does say 220 / 110 as its power sources. However there is no indication of wiring differences for each source. I am an electronics technician and have done a lot of wiring over the years on radiology equipment. It has been my experience that those two voltages, as inputs, are wired differently. Typically, one has two hots and a ground, the other has one hot, a ground, and a neutral. Since neutral and ground are essentially the same (for the 120v circuit), at the breaker box, where they go at the device being powered is important. I certainly do not want to burn up the motor but I also do not want to create a hazard.
Thanks for all the quick replies!
Thanks for all the quick replies!
Can you check the plug where he plugged it in?
SS 500(09/1980), DC3300, jointer, bandsaw, belt sander, Strip Sander, drum sanders,molder, dado, biscuit joiner, universal lathe tool rest, Oneway talon chuck, router bits & chucks and a De Walt 735 planer,a #5,#6, block planes. ALL in a 100 square foot shop.
.
.
Bob
.
.
Bob
- JPG
- Platinum Member
- Posts: 35457
- Joined: Wed Dec 10, 2008 7:42 pm
- Location: Lexington, Ky (TAMECAT territory)
You ARE correct re 'typical' 230v 'appliance'. Particularly so if it of the 'portable' variety and HAS a 'linecord' with a plug attached(3 or 4 wire depending on application).mada1 wrote:From what I have been told, by my wife's brother, this 10ER was definitely powered by 220v. The motor plate does say 220 / 110 as its power sources. However there is no indication of wiring differences for each source. I am an electronics technician and have done a lot of wiring over the years on radiology equipment. It has been my experience that those two voltages, as inputs, are wired differently. Typically, one has two hots and a ground, the other has one hot, a ground, and a neutral. Since neutral and ground are essentially the same (for the 120v circuit), at the breaker box, where they go at the device being powered is important. I certainly do not want to burn up the motor but I also do not want to create a hazard.
Thanks for all the quick replies!
However, motors of this size which ARE 230v or dual voltage(wired for 230v) do NOT have ANY use for the NEUTRAL therefore a separate NEUTRAL wire is NOT used. A typical linecord would have 3 conductors(HOT1 HOT2 GROUND).
The power switch needs to be a two pole so as to open BOTH 'hots' when switched OFF.
I will look for the motor wiring diagram for my 115/230v Goldie and post it(assuming I DO findit)!
╔═══╗
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
- JPG
- Platinum Member
- Posts: 35457
- Joined: Wed Dec 10, 2008 7:42 pm
- Location: Lexington, Ky (TAMECAT territory)
CAVEAT CAVEAT CAVEAT CAVEAT CAVEAT This wiring diagram is intended as an EXAMPLE; NOT to imply YOUR 10ER Motor is the SAME.
[ATTACH]3551[/ATTACH]
This is from a mid 60's GOLDIE. You can see that IF running 115v, the two winding leads are connected in Parallel. When running 230v, the windings are connected in Series. Notice BOTH poles of the power switch are used. I expect a SIMILAR method is used on the 10ER Motor.
I WOULD recommend keeping it as a 230V. I bought mine that way! NONE of the problems which abound in this forum regarding 'dimming lights', tripping breakers, only starting when adjusted for slow speed, etc. have occurred to me! Another advantage is that with a 230V branch circuit, it is unlikely to be shared with any thing else.
P.S. Since the current draw is 1/2 that when used on 115v, the wiring may be smaller(#14) and the circuit a 15A.
[ATTACH]3551[/ATTACH]
This is from a mid 60's GOLDIE. You can see that IF running 115v, the two winding leads are connected in Parallel. When running 230v, the windings are connected in Series. Notice BOTH poles of the power switch are used. I expect a SIMILAR method is used on the 10ER Motor.
I WOULD recommend keeping it as a 230V. I bought mine that way! NONE of the problems which abound in this forum regarding 'dimming lights', tripping breakers, only starting when adjusted for slow speed, etc. have occurred to me! Another advantage is that with a 230V branch circuit, it is unlikely to be shared with any thing else.
P.S. Since the current draw is 1/2 that when used on 115v, the wiring may be smaller(#14) and the circuit a 15A.
- Attachments
-
- motorwd.jpg (272.34 KiB) Viewed 13529 times
╔═══╗
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
Thanks for the diagram and info. I agree that it would be better to leave it at 230v due to the current draw, etc. The only barrier is for my son to get his landlord's permission to add a 230 circuit. Beyond that we still need to find out if he even has a 20 amp outlet available in his garage (for 115v). If not then a new circuit may be needed anyway, assuming that 15 amp would not work.
- JPG
- Platinum Member
- Posts: 35457
- Joined: Wed Dec 10, 2008 7:42 pm
- Location: Lexington, Ky (TAMECAT territory)
15A would probably work IF no other devices were on that branch. Running a dedicated 115v branch is an option(a 230v would be better). A 230v could be 15A but would require a 2 pole breaker. A 115v would only need a single pole breaker BUT should be 20A. PROS/CONS!:)mada1 wrote:Thanks for the diagram and info. I agree that it would be better to leave it at 230v due to the current draw, etc. The only barrier is for my son to get his landlord's permission to add a 230 circuit. Beyond that we still need to find out if he even has a 20 amp outlet available in his garage (for 115v). If not then a new circuit may be needed anyway, assuming that 15 amp would not work.
╔═══╗
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
I wish I had that kind of luck here. Since 10/08, when I got my first 10ER, I've watched eBay for auctions within 200 miles. In that time, I've seen ONE auction. And it just happened to be at a time when I didn't need to spend the money so I didn't bid.reible wrote:Hi,
Again it is location location location.
I've been looking for one as a birthday present for my older brother, to be used as a lathe, he has all the other normal tools (non-shopsmith). So I've been watching the normal outlets and have had some friends keeping their eyes open as well. This was for any shopsmith.... but the following were the results for 10er's in my area.
One ebay one came up for $199.99 ended with no bids...
Another came up for $149.95 ended with no bids...
I'm picking one up in a few hours (ebay buy) $75.00 and I was the only one to bid.
These were over the last month, and are only a sample of ones in my geographic area (driving distance). Can't say for other areas or other times.
Ed
- wlhayesmfs
- Platinum Member
- Posts: 667
- Joined: Fri Jul 21, 2006 10:50 am
- Location: Broken Arrow OK
The two basic motor I have found in the paper work on the er's are only 110. But to that same point I bought one from the original owner that the first thing he did was change it to a two speed 220 motor. I got both motors with it since the new original motor was only used a couple of time and still in a box. I gree with JPG on reading the motor and do what it says. Also I seen guys change plugs to only fit a dedicated plug like one of the guys stated already. I have a dedicated line for my MKV's since they seem to draw more.
Thanks
Thanks
Bill
Broken Arrow OK
MKV, 510, MKVll, 50th Anniversary 520 with Jointech saw train, Bandsaw, scroll saw, joiner, 6" Sander,Stand Alone Pin Router and Router Table, Strip Sander, Jigsaw & (4) ER's plus Jigsaw for ER. DC SS RAS

Broken Arrow OK
MKV, 510, MKVll, 50th Anniversary 520 with Jointech saw train, Bandsaw, scroll saw, joiner, 6" Sander,Stand Alone Pin Router and Router Table, Strip Sander, Jigsaw & (4) ER's plus Jigsaw for ER. DC SS RAS
I have a chance at getting a 10ER for $400.00 is that a good deal? Im just afraid that being so old it may be more of a problem than its worth. Am I wrong? would these be worth bothering with? what I mean is, bearings, bushings and such wear out.. will this be all sloppy and off and make bad cuts?
Wood worker wanna be with some tools, One deaf Aussie/Border Collie Mix, A Coonhound named Sam, twocats and a wife..lol 

On the surface, $400 seems high for a basic 10ER. Other factors though can affect the price. The factors besides location include whether or not it has a speed changer, 10ER jigsaw, 4E jointer with headstock mount and pulleys, the elusive lower saw guard, the also elusive lower belt guard and lastly the Power Mount adapter kit (includes 'A' and 'B' brackets, power coupler and headstock pulley with integral drive hub). And if it has the Power Mount adapter kit, there could be a belt sander, bandsaw, Mark V jigsaw, Mark V jointer and so on. In this area, 10ER's can generally be purchased for around $100 or less.zacker wrote:I have a chance at getting a 10ER for $400.00 is that a good deal? Im just afraid that being so old it may be more of a problem than its worth. Am I wrong? would these be worth bothering with? what I mean is, bearings, bushings and such wear out.. will this be all sloppy and off and make bad cuts?
Now the machine itself is built like a tank. All of the bearings can be replaced and the bearings are easy to find and fairly easy to replace. The ER is heavier than the Mark V (without the Power Pro upgrade) and with a speed changer has a wider speed range than the standard Mark V. My ER was purchased by my father in 1952 and it still hums along (quieter than a standard Mark V).
Good luck.
Rob in San Diego