The supplement to the PowerPro manual says that the PowerPro will trip a GFCI receptacle. I plug my PowerPro into one and it has never tripped.
I have a new Jet mini lathe with a variable speed DC motor, and it trips the same outlet every time the speed is increased to about 2/3 max.
I kind of like the idea of ground fault protection, so does anyone know of gfci outlets that can handle the DC motor, or will I just have to install a non-gfci outlet?
Thanks,
Mike
I have a new Jet mini lathe with a variable speed DC motor, and it trips the same outlet every time the speed is increased to about 2/3 max.
I kind of like the idea of ground fault protection, so does anyone know of gfci outlets that can handle the DC motor, or will I just have to install a non-gfci outlet?
Thanks,
Mike
Mike
I also have the Delta variable speed mini lathe and I have it in a GFCI receptacle and I have never tripped the GFI with the PP or the lathe. Do you have the 46-460 type one or two? I think that there were changes to the type two that corrected the problems. Try changing the breaker with "Made in the USA " hospital grade GFCI.
Bill V
PS you may try to tie some overhend knots in the power cord to add some inductance which may block some of the RF getting on the power cord.
I also have the Delta variable speed mini lathe and I have it in a GFCI receptacle and I have never tripped the GFI with the PP or the lathe. Do you have the 46-460 type one or two? I think that there were changes to the type two that corrected the problems. Try changing the breaker with "Made in the USA " hospital grade GFCI.
Bill V
PS you may try to tie some overhend knots in the power cord to add some inductance which may block some of the RF getting on the power cord.
Thanks, Bill
The lathe is a Jet 1221VS.
Shopsmith says that the PowerPro won't trip a GFCI breaker, but will a GFCI receptacle. I have a receptacle, but the PowerPro seems to work fine. I'll look into the hospital grade version, but in the meantime, the overhead receptacle that the garage door plugs into seems to not be gfci, and the lathe works fine there.
Thanks again,
Mike
The lathe is a Jet 1221VS.
Shopsmith says that the PowerPro won't trip a GFCI breaker, but will a GFCI receptacle. I have a receptacle, but the PowerPro seems to work fine. I'll look into the hospital grade version, but in the meantime, the overhead receptacle that the garage door plugs into seems to not be gfci, and the lathe works fine there.
Thanks again,
Mike
I cured my GFCI outlet problem by purchasing and installing a hospital grade GFCI outlet. I believe I was the first to point this out to Shopsmith, as they had never heard of the issue before. I was told that the shop at Shopsmith has all GFCI breakers - no special outlets.
Anyway, went to an electrical supplier store locally, after searching the internet, and requested the hospital type outlet. It solved the problem.
Anyway, went to an electrical supplier store locally, after searching the internet, and requested the hospital type outlet. It solved the problem.
Octogenarian's have an earned right to be a curmudgeon.
Chuck in Lancaster, CA
Chuck in Lancaster, CA
- JPG
- Platinum Member
- Posts: 35600
- Joined: Wed Dec 10, 2008 7:42 pm
- Location: Lexington, Ky (TAMECAT territory)
Do you know why a hospital grade receptacle is less prone the false gfci tripping with the power pro? AIUI the difference has to do with anti-tampering and plug retention.charlese wrote:I cured my GFCI outlet problem by purchasing and installing a hospital grade GFCI outlet. I believe I was the first to point this out to Shopsmith, as they had never heard of the issue before. I was told that the shop at Shopsmith has all GFCI breakers - no special outlets.
Anyway, went to an electrical supplier store locally, after searching the internet, and requested the hospital type outlet. It solved the problem.
╔═══╗
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
No! All I know is the change worked:) Purely empirical.JPG40504 wrote:Do you know why a hospital grade receptacle is less prone the false gfci tripping with the power pro? AIUI the difference has to do with anti-tampering and plug retention.
Octogenarian's have an earned right to be a curmudgeon.
Chuck in Lancaster, CA
Chuck in Lancaster, CA
- JPG
- Platinum Member
- Posts: 35600
- Joined: Wed Dec 10, 2008 7:42 pm
- Location: Lexington, Ky (TAMECAT territory)
charlese wrote:No! All I know is the change worked:) Purely empirical.
Wonder if it is a class 'B' which has a higher leakage current trip point.
Never mind, class B is not relevant to hospital receptacles.
╔═══╗
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
- JPG
- Platinum Member
- Posts: 35600
- Joined: Wed Dec 10, 2008 7:42 pm
- Location: Lexington, Ky (TAMECAT territory)
GFCI in a hospital setting is a mixed blessing. Surely protecting patients and personnel is important, but they have a history of 'nuisance' tripping. I cannot think of a place that nuisance tripping is more of a hazard than the leakage current. Nuisance tripping in a hospital would turn off life support equipment.
So I wonder if Chuck's hospital grade receptacle is less prone to tripping due to spurious leakage current.
So I wonder if Chuck's hospital grade receptacle is less prone to tripping due to spurious leakage current.
╔═══╗
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
- BuckeyeDennis
- Platinum Member
- Posts: 3814
- Joined: Tue Jul 24, 2012 10:03 pm
- Location: Central Ohio
I found a bit of info in a Levitron hospital-grade datasheet. It claimed improved immunity to nuisance tripping from high-frequency noise. And then I found a the same claim from Levitron on a NON-hospital grade GFCI.JPG40504 wrote:Do you know why a hospital grade receptacle is less prone the false gfci tripping with the power pro? AIUI the difference has to do with anti-tampering and plug retention.
I can personally attest that switching transients from motor drives, in conjunction with noise-suppression filters incorporating line-to-ground capacitors, will trip some GFCI's. To combat this, I once went so far as to specify an isolation transformer between the AC supply and some motor drives from a major manufacturer.
A true ground fault would result in 60Hz ground current. Motor drive noise is usually at least 8 kHz, with most of the energy way up in the higher harmonics.
Apparently, higher-quality GFCI's do a better job of ignoring the high-frequency stuff. It stands to reason that hospital-grade GFCI's need to be better. You don't want your ventilator shutting off for no good reason!
- JPG
- Platinum Member
- Posts: 35600
- Joined: Wed Dec 10, 2008 7:42 pm
- Location: Lexington, Ky (TAMECAT territory)
BuckeyeDennis wrote:I found a bit of info in a Levitron hospital-grade datasheet. It claimed improved immunity to nuisance tripping from high-frequency noise. And then I found a the same claim from Levitron on a NON-hospital grade GFCI.
I can personally attest that switching transients from motor drives, in conjunction with noise-suppression filters incorporating line-to-ground capacitors, will trip some GFCI's. To combat this, I once went so far as to specify an isolation transformer between the AC supply and some motor drives from a major manufacturer.
A true ground fault would result in 60Hz ground current. Motor drive noise is usually at least 8 kHz, with most of the energy way up in the higher harmonics.
Apparently, higher-quality GFCI's do a better job of ignoring the high-frequency stuff. It stands to reason that hospital-grade GFCI's need to be better. You don't want your ventilator shutting off for no good reason!
Way back when I was gainfully employed, every hour on the hour GFCIs tripped all over the place.
It was determined that the self correcting clocks were the cause. These clocks were designed to run slightly slow, and a signal was superimposed on the power line to trigger a self set to '0' minutes each hour change. This higher frequency signal was causing greater leakage current than the normal 60 Hz frequency.
I ran frequency tests on the GFCIs in use there and determined that at the clock signal frequency, the GFCIs tripped at less than 2 ma.
I forwarded that to the squareD plant down the road. They thought I was nuts! But then they did not have IBM/Simplex clocks! Not sure they realized the significance. I have to assume they were even more sensitive at higher frequencies.
That was a few decades back when GFCI were 'new'.
╔═══╗
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange
╟JPG ╢
╚═══╝
Goldie(Bought New SN 377425)/4" jointer/6" beltsander/12" planer/stripsander/bandsaw/powerstation /Scroll saw/Jig saw /Craftsman 10" ras/Craftsman 6" thicknessplaner/ Dayton10"tablesaw(restoredfromneighborstrashpile)/ Mark VII restoration in 'progress'/ 10E[/size](SN E3779) restoration in progress, a 510 on the back burner and a growing pile of items to be eventually returned to useful life. - aka Red Grange